Detecting digital input | LabJack
 

Detecting digital input

4 posts / 0 new
Last post
digital
digital's picture
Detecting digital input

I have a device that outputs a digital out (5V or 0V signal). I have connected the signal ground to the labjack's FIO0 ground, and the signal to FIO0. With the digital output both on and off, I only read '1' from the FIO0 input. Is this wired correctly?

LabJack Support
labjack support's picture
If the voltage from FIO0

If the voltage from FIO0 versus GND is < 0.8 volts it will read low.

https://labjack.com/support/datasheets/u6/appendix-a

Connect a DMM to FIO0/GND at the same time as your signal.  I suspect you will see that your signal is not pulling FIO0 below 0.8 volts.

Can you post a link to technical details for the signal?

digital
digital's picture
When I connect the multi

When I connect the multi-meter directly to the signal, it reads 0V or 5V. Connected to FiO0/GND, it reads 3.35V or 5V. I'm using http://www.watlow.com/F4T.cfm (See the digital I/O module under the F4T user guide: installation & troubleshooting).

LabJack Support
labjack support's picture
Looking at page 22 of the F4T

Looking at page 22 of the F4T user guide it does not look like it has push-pull (5V/0V) digital outputs.  Rather it has NPN or PNP outputs:

https://labjack.com/support/app-notes/open-collector-signals

From what you describe in your case it sounds like the output is switching between 5V and open (high-impedance) which would be PNP.  Try adding a 4.7k pull-down from FIO0 to GND which will hold FIO0 low when your signal is high-impedance.